200 Amp Service Main Panel

Status
Not open for further replies.

dereckbc

Moderator
Staff member
Location
Plano, TX
Someone remind me where in the code limits the number of branch circuit breakers that can be put into a 200 amp panel, or any other sized service panel for that matter. I know 42 is the answer, but for the life of me my tired old brain cannot remember.
 
Last edited:
Maybe because I am hearing from an associate of using a 60 position 200 amp panel. Hence the point of my question and only have a 2005 book. So before I rebute him I do not want to get caught out of date. Those things happen when you get old :grin:
 
Last edited:
408.35, in the 2005 edition. Removed in the 2008 edition. Also, if it was not a "Lighting and Appliance Panelboard," meaning that less than 10% of its breakers were 30 amp or lower with a connection to the neutral, then the 42 circuit limit did not apply. Even in 2005, you could have 20 three phase motor circuit feeder breakers in a single panel, for a total of 60 breaker positions.
 
Last edited:
Maybe because I am hearing from an associate of using a 60 position 200 amp panel. Hence the point of my question and only have a 2005 book. So before I rebute him I do not want to get caught out of date. Those things happen when you get old :grin:

It is legal, 408.34 and 408.35 are gone in the 2008. If you are 2005 then they apply.

2008

408.30 General. All panelboards shall have a rating not
less than the minimum feeder capacity required for the load
calculated in accordance with Parts II, III, IV, or V of Article
220 as applicable.
 
Thank you guys. 2008 cycle is what I was missing. Time to get a new book, 2011 cycle. This ole dog needs to learn some new tricks. :cool:
 
The only restriction now is "listing and labeling"
 