200 amp service

Status
Not open for further replies.

enireh

Senior Member
Location
Canyon Lake,TX
our service at the pole caught fire and burned shooting flames out of the box. there was a 200 amp main that fed the house 150' away what would cause it to flame up like that a new service is in now and with everything running there is 87 amps on a and b phase and 9 amps on the neutral
 
our service at the pole caught fire and burned shooting flames out of the box. there was a 200 amp main that fed the house 150' away what would cause it to flame up like that a new service is in now and with everything running there is 87 amps on a and b phase and 9 amps on the neutral

So there was a fire on a pole and later sparks came out of a box 150' away?

If I understand this correctly I think the most likely cause was the insulation melted off a live conductor at the pole and that live conductor touched the grounded conductor heading too that box that sparked. That placed a large current on the grounded conductor and one of the terminations related to it could not handle the current.
 