200 amp service

Status
Not open for further replies.

jday

New member
I have installed a new 320/400 amp meter combo for an addition. The 400 amp meter combo has two 200 amp main breakers. One is feeding the existing panel and the other is for a new 200 amp panel servicing the addition. The new panel is approximately 100 feet away. What are the proper wire sizes? Also, should I have 3 conductors with a grounding rod at the new panel or 4 conductors carrying the ground from the meter.
 
This thread had been temporarily closed. This action was taken because the nature of the question and the occupation shown in the Original Poster's profile raised a concern that this may have been an attempt by a Do It Yourself person to obtain "how-to" information.

In an exchange of Private Messages, the Original Poster has provided assurances that he is a licensed electrician or electrical contractor or is otherwise authorized to perform electrical installation work, and that the question had to do with a business issue. Therefore, the thread is being returned to the active area. I offer an apology to the OP for the inconvenience and the delay.
 
The service is the meter main with the two 200A disconnects. That is where the ground electrodes should connect and not at any down stream panel.

You need to feed each 200A panel with 4 wires and make sure the neutral and ground are not bonded in either down stream panel. This may be a pain in the existing 200A panel if it is old and is a bit short on neutral and ground bus terminals. Could also get ugly if the wires are too short and you need to wire nut on some pigtails.

Wire size is determined by the source feeder breaker, which is 200A in this case (unless you want to use feeder tap rules, and you probably don't). So for 200A, you use 3/0 copper (with #6 equipment ground). If going with aluminum, you use 4/0 if the calculated load is 180A or less, or 250 KCMil if you're pushing the full 200A. Use a #4 equipment ground if using aluminum.
 