Here we were told that the panelboard shall have a rating as was calculated just as Torcho has pointed out. The size of branch circuits and their overcurrent protection will be based on the calculated size of their individual loads and it is not uncommon for these to add up to be a lot more that the feeder circuit and the feeder overcurrent protective device.408.30 General. All panelboards shall have a rating not less than the minimum feeder capacity required for the load calculated in accordance with Article 220.
This limit to 42 overcurrent device rule is for lighting and appliance branch-circuit panelboard ONLY and will not apply to a power panelboard.408.35 Number of Overcurrent Devices on One Panelboard.
Not more than 42 overcurrent devices (other than those provided for in the mains) of a lighting and appliance branch-circuit panelboard shall be installed in any one cabinet or cutout box.
You have confused me a little, given that the title of the thread uses the word "service," and given wording of the question. Your profile describes you as a "machinery controls designer," and you are asking about overloading a "service." That word relates to the main panel at a home or office or industrial building, and not to any panel that might be associated with a machine.Originally posted by beardog:Is there a code on the total circuit-breaker amperage.
No you cannot. Can you assume that it is safe to back out of your driveway blindfolded, if you have done it every day for a month, and it has never resulted in an accident?Can you assume that it's not over loaded if it never trips the main breaker?