tomgquinn
Member
- Location
- West Virginia
I am installing a 200 amp subpanel in an old school building. The panel will feed a kitchen.
200 amp subpanel panel is 100 ft away from main 400 amp panel. The panel is an old GE with solid copper bussbars about 1 1/2 wide and 3/8 inch thick.
There is no snap in 200 amp breaker listed for installation in this panel... however, There are lugs on the bussbars (after the 400 amp breaker) rated to hold up to 4/0 wire.
If i understand code correctly, it would be appropriate to place a 200 amp disconnect within 6 feet (actually about 6 inches)away from the 400 amp panel, attach 3/0 copper from lugs on 400 amp bussbars to line side of 200 amp disconnect, and a 3/0 between the neutrals. A #4 copper ground conductor should also be run and at the disconnect the ground and neutral are split.
Q:: Because the 200 amp disconnect is within 6 feet of the 400 amp panel, the feeds can be sized based on the lower 200 amp overcurrent device. (3/0 instead of larger.)
Q::If I am reading UGLY book right... (no NEC available, sorry) The fourth (grounding)conductor would be #4 copper.
Then, from the disconnect, 3/0 copper and #4 ground are run (in 2" EMT) to the 200 amp subpanel and agin, the neutral and ground remain seperated.
sound ok?
200 amp subpanel panel is 100 ft away from main 400 amp panel. The panel is an old GE with solid copper bussbars about 1 1/2 wide and 3/8 inch thick.
There is no snap in 200 amp breaker listed for installation in this panel... however, There are lugs on the bussbars (after the 400 amp breaker) rated to hold up to 4/0 wire.
If i understand code correctly, it would be appropriate to place a 200 amp disconnect within 6 feet (actually about 6 inches)away from the 400 amp panel, attach 3/0 copper from lugs on 400 amp bussbars to line side of 200 amp disconnect, and a 3/0 between the neutrals. A #4 copper ground conductor should also be run and at the disconnect the ground and neutral are split.
Q:: Because the 200 amp disconnect is within 6 feet of the 400 amp panel, the feeds can be sized based on the lower 200 amp overcurrent device. (3/0 instead of larger.)
Q::If I am reading UGLY book right... (no NEC available, sorry) The fourth (grounding)conductor would be #4 copper.
Then, from the disconnect, 3/0 copper and #4 ground are run (in 2" EMT) to the 200 amp subpanel and agin, the neutral and ground remain seperated.
sound ok?