Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
My boss has decided to have me install a 200 ampere sub pannel to a building, which I have completed along with all necessary branch circuits and breakers.
However, he has decided to feed the sub panel fed from a service disconnect panel. The run is 300 feet and he is using aluminum # 2 AWG conductor (specific type of insulation unknown but I will look for the conductor type and post it here when I find it).
He has also decided to use pvc (schedule 40? at 1 and 1/4 inch which will fit the conductors and equipment ground conductor to be within 40 percent of conductor fill
My questions are:
The #2 AWG wire will have an ampacity before correction at 115 amperes at 75 degrees Celsius and will be too small for the 200 ampere sub pannel even considering any possible 85% reduction demand factors for feeders similar to services and if relevant to feeders or allowed
Are not feeders supposed to be sized either to accommodate the largest load or be sized to 125 percent of continuous loads plus 100 percent of non continuous loads or final option to be sized for ampacity after temperature correction and conductor derating?
NEC says Aluminum is not to be within 18 inches of dirt or in wet locations such as underground conduit but NEC code contradicts this by also saying NEC 300.6 B
Aluminum in apparatus embedded in concrete or direct contact with earth must have supplemental corrosion protection?
However, he has decided to feed the sub panel fed from a service disconnect panel. The run is 300 feet and he is using aluminum # 2 AWG conductor (specific type of insulation unknown but I will look for the conductor type and post it here when I find it).
He has also decided to use pvc (schedule 40? at 1 and 1/4 inch which will fit the conductors and equipment ground conductor to be within 40 percent of conductor fill
My questions are:
The #2 AWG wire will have an ampacity before correction at 115 amperes at 75 degrees Celsius and will be too small for the 200 ampere sub pannel even considering any possible 85% reduction demand factors for feeders similar to services and if relevant to feeders or allowed
Are not feeders supposed to be sized either to accommodate the largest load or be sized to 125 percent of continuous loads plus 100 percent of non continuous loads or final option to be sized for ampacity after temperature correction and conductor derating?
NEC says Aluminum is not to be within 18 inches of dirt or in wet locations such as underground conduit but NEC code contradicts this by also saying NEC 300.6 B
Aluminum in apparatus embedded in concrete or direct contact with earth must have supplemental corrosion protection?