We are building a house with service from the road to a 400 amp meter can. The can has two 200 amp breakers, one to serve the shop and the second to serve the house so the shop and house breaker boxes are sub-panels.
I'm okay with the shop as that breaker box is on the other side of the wall of the meter can.
Our state/utility is still using 2014 NEC for code compliance.
My Questions
The 200 amp service from the breaker in the meter can to the house will run 100' underground.
1) Will 4/0 Alu support the house or do I need to step up to 250 kcmil?
2) Since this is a sub-panel, do I need to pull 4 conductors or can I set two ground rods at 6' at the house and delete the ground back to the meter can?
3) Can I do this in 2" PVC?
I appreciate in advance the help. In the work I do, electrical overlaps into it every day but I'm still learning my way around the NEC and in this case, don't want to dump a bunch of money and effort on wire too small.
I would appreciate code references in any response to help in my continued learning.
Again, thanks to all.
We are building a house with service from the road to a 400 amp meter can. The can has two 200 amp breakers, one to serve the shop and the second to serve the house so the shop and house breaker boxes are sub-panels.
I'm okay with the shop as that breaker box is on the other side of the wall of the meter can.
Our state/utility is still using 2014 NEC for code compliance.
My Questions
The 200 amp service from the breaker in the meter can to the house will run 100' underground.
1) Will 4/0 Alu support the house or do I need to step up to 250 kcmil?
2) Since this is a sub-panel, do I need to pull 4 conductors or can I set two ground rods at 6' at the house and delete the ground back to the meter can?
3) Can I do this in 2" PVC?
I appreciate in advance the help. In the work I do, electrical overlaps into it every day but I'm still learning my way around the NEC and in this case, don't want to dump a bunch of money and effort on wire too small.
I would appreciate code references in any response to help in my continued learning.