Mike Fleming
Member
- Location
- Maryland
I have a contractor who has installed a trough over 5 panels, there are over 200 current carrying conductors in said trough. They have pulled #10 wire but at 35%(Table 310.15(B)(2) I come up with that #10 being good for 14 amps, the contractor says the loads will never go over that and the OCPD is a 20 breaker. Am I correct in thinking that these circuits must go on a 15 amp breaker?