thunder15j
Member
- Location
- Cali
I am designing a feed to a 200 HP 480 volt motor that will power a water pump that will be running continuously, 3 hours or more. The motor will not be pulling full load.
NEC table 240.15 200 HP motor feed= 240 amps; cont duty. 1.25x = 300 amps. 350 mcm. $5.30 ft +/- cu
Paralleling 2/0 cu: 2/0 @ 90c = 195 amps; 4-6 conductors in raceway (310.15 B 2 a) .8 x 195=156 amps. 2 wires per phase @ 2 x156= 312 amps. $ 1.96/ft x 2 =3.92/ ft .
Substantial savings can be gained by paralleling the wire, especially one that might be several hundred feet long The method of motor control will be a soft-starter with bypass. I am always concerned about any heat transfer to the electronics of the controller especially with a soft starter. I do realize that voltage drop needs to be addressed and also labor costs. In this particular installation. neither is a factor.
My only real concern here is the fact that because I used the 90 degrees Celsius rating for the wire ampacity, is there a risk of any heat being conducted to the starter.
Any remarks on my design would be appreciated. Thank you
NEC table 240.15 200 HP motor feed= 240 amps; cont duty. 1.25x = 300 amps. 350 mcm. $5.30 ft +/- cu
Paralleling 2/0 cu: 2/0 @ 90c = 195 amps; 4-6 conductors in raceway (310.15 B 2 a) .8 x 195=156 amps. 2 wires per phase @ 2 x156= 312 amps. $ 1.96/ft x 2 =3.92/ ft .
Substantial savings can be gained by paralleling the wire, especially one that might be several hundred feet long The method of motor control will be a soft-starter with bypass. I am always concerned about any heat transfer to the electronics of the controller especially with a soft starter. I do realize that voltage drop needs to be addressed and also labor costs. In this particular installation. neither is a factor.
My only real concern here is the fact that because I used the 90 degrees Celsius rating for the wire ampacity, is there a risk of any heat being conducted to the starter.
Any remarks on my design would be appreciated. Thank you