A 200 HP VFD may have SCRs in the rectifier bridge that are phase controlled to slow down the charging of the bus capacitors, instead of using a precharge resistor.
Yes, I used to work a lot with Lenze (German) equipment and their ECS Servo Power supplies did this. They used thyristors iirc and timed the zero crossings to turn on the thyristor for only a short time, connecting the AC Mains to the rectifier bridge.
This did 2 things - it allowed the Power Supply to monitor the DC bus voltage and look for something like 20 to 30 volts DC. If it saw that voltage, it assumes the DC bus connected downstream to the Servo drives is not shorted and then it will close a set of relays to allow all 6 diodes to charge up the DC bus from the AC Mains. Having the DC bus slightly charged helps reduce the "shock" of surge current that would otherwise happen when you try and power up completely discharged DC bus caps. (Most drives use a pre-charge resistor for this). At least, that's what I remember it did.
If, however, the Power Supply does NOT see the DC bus charging to 20 or 30 volts it will not close the relays in, and the drive will indicate a specific error - alerting the user to a possible short in the DC+ to DC-, or either end to ground.
Pretty neat system, and it took a second or 2 tops at startup. It avoids the occasional disaster when there is a problem on the DC bus in a Servo and the Power Supply just comes in full beans. For example, a mis-wired DC bus is rare -but can happen - especially when commissioning a system (Sunday wired to Monday).
It did have a drawback for us though at several sites. The electronics in the Power Supply first measure the zero crossings in the AC Mains and they must pass a sort of quality test. Meaning timing and angles. The thyristors must be turned on close to the zero crossings or risk damage if switched on during some larger energized part of the sine wave. If the controls did not like "quality" of the AC Mains, they won't even start the initial DC bus test, and throw a specific error. Depending on what site we were commissioning, the AC Mains were failing this test (either poorly regulated POCO, or site's machinery creating phase shifts). Anyway, we went back and forth with Lenze Germany about this, and their reaction initially was to fix the site power issues. And we understood that stance. But in the end, they developed a new revision of firmware that had looser tolerances for our crappy "American" power.
Just guessing here of course, but like Synchro is suggesting above, if condensation got around the trigger part of an SCR and caused it to conduct at start up when it was not supposed to...