So it's asking for a 200% neutral but then give the neutral size which is the same size as the hots. The neutral should be larger correct?
How would you size it? Double the ampacity of the CCC's? Thanks.
No, a 100 amp hot conductor and a 100 amp neutral conductor would be the same. A 100 amp hot conductor with a 200% neutral would be a 200 amp neutral conductor.This may be a dumb question, but wouldn’t a 200% neutral be the same size as the hot anyway?
“normally” a 100% neutral would be half size of the “hots”wouldn’t it?
I see what your saying regarding the amps, but wouldn’t a 100% RATED neutral would be half size?No, a 100 amp hot conductor and a 100 amp neutral conductor would be the same. A 100 amp hot conductor with a 200% neutral would be a 200 amp neutral conductor.
UPSIf those are both the same feeder then it would require 5-#2/0 not 4, and 2 EGC's unless you're using the raceway as one EGC. Might not fit in a 2" either. What is the IG for?
No, a 100% neutral would be equal in size to the ungrounded conductor. For a 120/240 volt system the neutral will carry the current imbalance of the two hot legs which could theoretically be 100% of the current in one hot leg.I see what your saying regarding the amps, but wouldn’t a 100% RATED neutral would be half size?
so if (say residential) needed 4/0 hot, a 100% rated neutral would be 2/0, correct?
a 200% would be a 4/0 neutral.
Does this make sense the way I’m seeing this?
Why would it be 2 neutrals ? You stated below that a 200% neutral would be twice the ampacity of the hots.If those are both the same feeder then it would require 5-#2/0 not 4, and 2 EGC's unless you're using the raceway as one EGC. Might not fit in a 2" either. What is the IG for?
You have:Why would it be 2 neutrals ? You stated below that a 200% neutral would be twice the ampacity of the hots.
Yes, I understand the math behind it. I’ve calculated triplens as high as 150% on some systems, but I’m in agreement with others triplen addition that high is hard to accomplish in the real world.No, a 100% neutral would be equal in size to the ungrounded conductor. For a 120/240 volt system the neutral will carry the current imbalance of the two hot legs which could theoretically be 100% of the current in one hot leg.
That is true, but you obviously would be getting no real power from the L-N legs with the inductor and capacitor. So as you say, I don't think this would be found in practice.E.g. if I understand correctly, a pure capacitor load and a pure inductor load would each phase shift 90 degrees in opposite directions. So then if you have a resistor, an inductor and a capacitor arranged with each L-N on a 3 phase supply, the current waveforms could be only 30 degrees apart (60 degrees between the capacitor and the inductor). Which if they are all equal magnitude, would sum to 1 + √3 times that magnitude, instead of 0 for the case of 3 resistors.
You could have a phase shift between the load current and the applied voltage greater than 90 degrees, but then the real part of the impedance would likely be negative (i.e., a negative resistance). In such a case, the load would be supplying real power to the source instead of the other way around. It could still be a linear load but it would not be a passive load.What's the maximum phase shift you can get from a linear load?