I have system which is requesting a 200% neutral rated panelboard that is feeding some switching power supplies. My question stems from how far back upstream does the neutral need to be rated 200%.
The general setup is a 480V-208V 3ph stepdown transformer. There will be a 208V-3ph 600A panel which has a mixture of continuous and non-continuous feeds. Out of that I will be feeding a 200A panel which has 125A non-continuous switching power supplies which is being specified to have a 200% rated neutral. Does the neutral only have to be rated for 200% back to my original 600A panel or is it all the way back to the transformer? Am I mistaken to think that the 600A neutral would be 200% rated when referring to the 200A panel? Any suggestions on places to research would be appreciated.
The general setup is a 480V-208V 3ph stepdown transformer. There will be a 208V-3ph 600A panel which has a mixture of continuous and non-continuous feeds. Out of that I will be feeding a 200A panel which has 125A non-continuous switching power supplies which is being specified to have a 200% rated neutral. Does the neutral only have to be rated for 200% back to my original 600A panel or is it all the way back to the transformer? Am I mistaken to think that the 600A neutral would be 200% rated when referring to the 200A panel? Any suggestions on places to research would be appreciated.