kspousta
- Northern, AZ
- Semi-retired contractor, helicopter pilot, IT guy
Hope this is the right place to post this. A search netted me some "confusing" answers so I hope you all can get me squared away..
Built a pool house out back. I need to put a 100A subpanel out there to power the pool equipment and the pool house itself. The run from the main panel (200A) is just about 200' and I've got 1.5" PVC conduit run already.
Since the pumps require 220V, I know I'll need two "hots" along with a neutral and a ground. 220 circuits will use double pole breakers, 110 circuits (GFCI) will need single pole breakers. I also know I need to keep the neutrals and grounds separate in the sub panel. I have some questions...
Do I need a ground rod at the subpanel or is the ground tie to the main panel sufficient?
What size feed wire to keep the voltage drop to a minimum? I read somewhere one should aim for no more than 3% drop..
To feed this subpanel, should I drop in a 100A breaker at the main, or use pass through lugs and put a 100A "main" breaker at the subpanel?
Total breakers at the subpanel will be 7.. Three 220s and one 110 for the pool equipment and three 110s for the pool house itself.
Am I on the right track here? Anything I missed or am completely incorrect on? I'm in CA BTW
Thanks!
Thanks!