I'm involved on a project; incoming power to the customer facility (our machine) is higher than expected (496 VAC). After tapping primary side to max voltage, our expected 220 VAC is coming in at 236. Normally not an issue; but we have some Fanuc LR mate robots who seem to like a lower voltage, and are giving us some regenerative power faults. After changing to an alternate power supply (power tapped from another location for short term use), robots prefer to run closer to 200-208 VAC without issue.
I'm looking to install a second transformer (277 input and <220 output, single phase) in series with our present machine transformer. I have found one through our supplier; and can't afford putting in a higher end constant voltage transformer (looking at 3KVA), and $3000 is out of budget.
Ideally, we would want our voltage to the robots at 200 VAC; and with all calculations; I'm coming up at about 220 VAC for our robot supply. Is there a better way to slice this, getting
Any help greatly appreciated.
I'm looking to install a second transformer (277 input and <220 output, single phase) in series with our present machine transformer. I have found one through our supplier; and can't afford putting in a higher end constant voltage transformer (looking at 3KVA), and $3000 is out of budget.
Ideally, we would want our voltage to the robots at 200 VAC; and with all calculations; I'm coming up at about 220 VAC for our robot supply. Is there a better way to slice this, getting
Any help greatly appreciated.