2000 amp 120/208 service grounding requirement

Status
Not open for further replies.

erwin71

Member
:?
MY question is what would the grounding requirement be for a 2000 amp meter main. code defines >25 ohms.
Two ground rods?
ground ring ?
:?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
:?
MY question is what would the grounding requirement be for a 2000 amp meter main. code defines >25 ohms.
Two ground rods?
ground ring ?
:?

Unless this 2000 amp service is freestanding the building would likely have a CEE which means you would need to connect to that with a minimum of #4 copper as the GEC.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
We do a lot of freestanding ag services. It's not uncommon to have a 2000 amp 480v service with just a couple grounds rods tied together with some #4 bare CU.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We do a lot of freestanding ag services. It's not uncommon to have a 2000 amp 480v service with just a couple grounds rods tied together with some #4 bare CU.

Could be that's why I mentioned it but for every one of them there's probably 1000 that are not freestanding. I'll go with the odds and say that it's the latter. :)
 