scott minter
Member
- Location
- Kennedy Space Center, Florida
- Occupation
- Associate Engineer
Hi I have a 2000 amp breaker at my facility it is being fed with 5 runs of 600 kcmil per phase
it is 480 volts. onthe load side of the breaker it has 6 spaces (lugs) per phase, i am only utilizing
5 as i said. Working under the tap rule could i land 1 more 600 kcmil on the breaker and run it
10 feet or less to a 400 amp fused dissconnect. When this new disconnect would be in use the
larger loads inside would not be.