A Square D/ Schneider 2000 ampere main circuit breaker in the service entrance switchboard trips every time there is a power outage, not when power is restored, but when utility power is interrupted. A 2000 amp service entrance rated automatic transfer switch, open transition, with a main breaker has been installed ahead of the 2000 amp main circuit breaker in the SE switchboard. The main circuit breaker in the ATS never trips on power outage but the switchboard breaker does. In testing, the ground fault protection was disabled and the instantaneous trip setting was dialed up to maximum but the switchboard circuit breaker continues to trip on interruption of power. Any ideas on what is causing this other than a defective breaker or trip unit?