He has a 2000 amp M/B service and was under the impression that he could install a set of 500 Cu. in his each of his 3" Sch 80 PVC conduits.
Once he was informed his 500s would not be sufficient for the 200 amp service, we were looking for a way to save the install.
Unless I made a mistake, he could install (6) 250s with a 1/0 Neutral in each conduit.
(6)250s would derate to 232 amps. 10 conductors exceed his 2000 amp requirement.
(6)250 THWN-2 + (1) 1/0, in each 3" Sch 80 {(6) X .3970 = 2.382 + (1) .1855 = 2.5675}
3" Sch 80 allows 2.577
anyone see an error in the plan ?