Re: 2000 amp SERVICE
Butch,
Is the grounded conductor a current carrying conductor in this service? It is a current carrying conductor only if a majority of the load in nonlinear. If the load is nonlinear, the 4 sets of 350s are only good for 1120 amps, not 1200.
If the grounded conductor is not a current carrying conductor, 10 350kcmil will fit in a 4" conduit. The 90?C ampacity (for derating) is 350 amps. You could install 8 350's in each raceway with a total ampacity of the circuit of 2240 amps. If the neutral of the service is a current carrying conductor, then the ampacity of the 4 conduits each with 8 350's would be 1960 amps. You are not permitted to round up, but if there is more than one service overcurrent protective device and if the calculated load is 1960 amps or less you could still use this set up. If the calculated load is above 1960 amps or if there is only one service OCPD rated at 2000 amps, then you could replace the 350 with 2 sets of 400 kcmil in each of the 4 conduits. This would give you an circuit ampacity, assuming a current carrying grounded conductor, of 2128 amps.
It sounds like you want to install the new 500s in parallel with the existing 350s. That would be a violation of 310.4. All of the conductors in parallel must be of the same size and type.
Don