For the referenced section of the 2000 NEC Code (680.51(B)), was the max voltage to operate a submersible pump 300 volts as it is in the current code, or was a higher voltage specified? Thanks for the help.
 
Welcome to the forum.

First off there is no 2000 NEC.

I looked in the 1999 NEC in section 680-51(b) and the maximum operating voltage between conductors for submersible pumps is 300 volts.

Hope this helps,

Chris
 