If they are magnetic ballasts, I hope they don't all come on at once, or you might be tripping that 225A MCB. Solid state ballasts probably have less inrush though.
Sent from my SM-G900V using Tapatalk
Ditto that. We had 6 26KW (13 2kW bulbs each, 156kW total load) lighting towers for site lighting at a plant I used to work at. They all came on at once, which would frequently cause the blowers or centrifuges to trip off-line.
~~~~~~~~~~~~~~~~~~~~
Anyway, a 225A 3ph 208V panel is good for 81kw. 40 bulbs if the ballasts were perfect (1.0pf), 32 (80%) if they are continuous loads, and 30 if the ballasts are .925pf or better. 30 would also give you perfect load distribution, with 10 on AB, 10 on AC, and 10 on BC.
Why 208V with 2000W bulbs? At 10A draw, even #8 is only good to 450' if VD has to stay at 3% or better. Also, a cursory search of 2000W ballasts didnt show any that could run at less than 277V.