In most cases the neutral would not need to be counted as a current carrying conductor, so you would be OK (2 X 380=2280). Many times this is a judgment call depending on the types of load. If the decision is made that the neutral counts, then you would be a little shy (6 X 380 X .8=1824).I am feeding a 2000 Amp MDP that has a Main Breaker in a school. Will the conductors in each conduit (6 sets of 3 500 MCM Hots, 1 500 MCM Neutral and 1 Ground) have to be derated?
I expect that a number of AHJs will say that the school has lighting and a large computer load that is all non-linear and that may be a majority of the load.I see no reason to count the neutral as a CCC on a school service.
Why would you worry about 120 volt neutral loads on the 277/480 volt service?
I also would asume they'll have a stepdown transformer to get 208/120Y . which means the SE neutral will have no "load". unless the lights will be 277
Good point, I overlooked the voltage when I posted.Why would you worry about 120 volt neutral loads on the 277/480 volt service?
Dear texie.. I dont understand the followings: (2 X 380=2280) and (6 X 380 X .8=1824). Would you please explain to me? please refer to the code/section.. I just want to learn :huh:In most cases the neutral would not need to be counted as a current carrying conductor, so you would be OK (2 X 380=2280). Many times this is a judgment call depending on the types of load. If the decision is made that the neutral counts, then you would be a little shy (6 X 380 X .8=1824).
Dear texie.. I dont understand the followings: (2 X 380=2280) and (6 X 380 X .8=1824). Would you please explain to me? please refer to the code/section.. I just want to learn :huh:
why MCM but not kcmil?
the 380 is current Ampacity for 500 kcmil @ 75 dgree C. right?
Dear texie.. I dont understand the followings: (2 X 380=2280) and (6 X 380 X .8=1824). Would you please explain to me? please refer to the code/section.. I just want to learn :huh:
why MCM but not kcmil?
the 380 is current Ampacity for 500 kcmil @ 75 dgree C. right?
many thanks..Texie just had a typo, he meant 6 x 380= 2280.
MCM is just the old version of kcmil.
The .8 is for derating, if required, for 4 or more CCC.
Table 310.15(B)(3)(a) Adjustment Factors for More Than
Three Current-Carrying Conductors in a Raceway or Cable
Yes, 380 is the ampacity of 500 kcmil @ 75C.