I'm not too proud to say I don't know everything and I could research this for hours if necessary, but I figured Id ask some of you that may know within seconds.
What I do know is these setting are intended to fine tune specific characteristics of either AIC ratings or other sensitive elements within an electrical wave or noise spectrum.
Here are some images of a project I went to today of a long time customer, they had a rooftop 40A 3 phase AC with issues, and since the fiasco of messing with the unit from the AC Techs they've inadvertently tripped the 2000A main 3 times within 3 weeks, point being the AC to me seems to be the culprit.
My answer would be to isolate the power to the troubled AC and see if the Main continues to trip; If it continues to trip with no AC connected then the 2000 A main breakers sensitivity settings may simply need to be recalibrated or moved to a less volatile setting, although the engineers may of needed these specific settings for highly sensitive equipment. I believe without the engineering specs raising the tolerances of this breaker would ease up on the overly sensitive tripping.
The AC breaker or fuses really should trip before the entire facilities power system.
My question can some of you point out in layman's terms these setting and maybe a scenario of their intent. I know a lot to ask and I wont hold you to it but I figure before I do research more hands on experience from the group couldn't hurt.
Thank you in Advance.
What I do know is these setting are intended to fine tune specific characteristics of either AIC ratings or other sensitive elements within an electrical wave or noise spectrum.
Here are some images of a project I went to today of a long time customer, they had a rooftop 40A 3 phase AC with issues, and since the fiasco of messing with the unit from the AC Techs they've inadvertently tripped the 2000A main 3 times within 3 weeks, point being the AC to me seems to be the culprit.
My answer would be to isolate the power to the troubled AC and see if the Main continues to trip; If it continues to trip with no AC connected then the 2000 A main breakers sensitivity settings may simply need to be recalibrated or moved to a less volatile setting, although the engineers may of needed these specific settings for highly sensitive equipment. I believe without the engineering specs raising the tolerances of this breaker would ease up on the overly sensitive tripping.
The AC breaker or fuses really should trip before the entire facilities power system.
My question can some of you point out in layman's terms these setting and maybe a scenario of their intent. I know a lot to ask and I wont hold you to it but I figure before I do research more hands on experience from the group couldn't hurt.
Thank you in Advance.