I have a retail installation where fluorescent strip lights are being suspended roughly 5' below and open structure by aircraft cable. The power for each of these comes from a j-box mounted to the structure directly above via an SJ cord down to the ballast compartment. The fixture's weight is completely suspended by the cable and the SJ cord is not concealed in any way since there is no ceiling.
The local code official is stating that this installation violates section 400.8 of the 2002 NEC. The only possible explanation I can find for his judgement is paragraph (1) since this is "fixed wiring" for this permanent fixture. However, paragraphs (1) and (2) of section 400.7 specifically state that flexible cords shall be used for "Pendants" and "Wiring of Luminaires" and section 400.8 says, " Unless specifically permitted in 400.7 flexible cords shall not be used for the following..."
Am I misunderstanding something here? This is not related to paragraphs 2,3,5 or 6 since everything is exposed and it doesn't violate paragraph 4 since the wire is not attached to any building surfaces... and besides, section 400.7 specifically allows this type of installation.
The local code official is stating that this installation violates section 400.8 of the 2002 NEC. The only possible explanation I can find for his judgement is paragraph (1) since this is "fixed wiring" for this permanent fixture. However, paragraphs (1) and (2) of section 400.7 specifically state that flexible cords shall be used for "Pendants" and "Wiring of Luminaires" and section 400.8 says, " Unless specifically permitted in 400.7 flexible cords shall not be used for the following..."
Am I misunderstanding something here? This is not related to paragraphs 2,3,5 or 6 since everything is exposed and it doesn't violate paragraph 4 since the wire is not attached to any building surfaces... and besides, section 400.7 specifically allows this type of installation.