Re: 2002 NEC Annex D Example D1(b)
OK, now I understand your question, and it has taken me some time to work out an answer. I think this is another example of an Example that gives clues without giving us explanations. Let?s look at three such ?clues.? First, in deriving the 61 amp neutral load, Example D(1)(a) did not tell us which circuits were connected to Line A and which to Line B. Secondly, Example D(1)(b) connected the disposer to Line B (why not A?). Finally, Example D(1)(b) showed the 115V A/C Unit and the dishwasher in the same row (why not on two separate rows?), and disregarded the neutral contribution of the smaller of the two loads. Now, what can we infer from these clues?
We must first realize that this type of calculation should be done in the office, long before an electrician shows up at the site to wire the circuits. If the Example showed the disposer on Line A, you would not have questioned the addition of the 12 amps to the 8 amps. But nothing in the code compels the electrician to connect the disposal to Line B. Similarly, nothing in the code compels the resident to run loads in such a way as to maintain a balanced loading. Since we don?t know during the initial calculation which loads will be connected to which Line, and since we never know exactly how the resident will be running the loads, the calculation must account for the ?worst case.? That forces us to size the conductors for the ?worst case.? But what is the ?worst case?? It is all loads connected to a single Line, and therefore the neutral carrying load from every single circuit. That is why the example includes the neutral?s 8 amps (i.e., from the disposer connected to Line B), even though it is not associated with the same ?one ungrounded conductor? that is shown to be carrying the 12 amps (i.e., from the A/C unit connected to Line A).
That only leaves us with the question of the A/C Unit and the dishwasher. Why does the Example not show both the 12 amps and the 10 amps? Why does it show only the larger of the two? I think the asterisk after ?air conditioning unit? (and the related footnote) represents an inadequate attempt to explain the design intent. I also think that the code is using this Example to acknowledge that there will be some efforts to balance loads, so that we need not count each and every load individually. In other words, it is no longer strictly a ?worst case,? but rather more like a ?worst-case-with-some-sanity-included? type of case. Let me expand the Example to list a total of 7 specific 120v loads (instead of the three ? the 12 amp, the 10 amp, and the 8 amp). Let me add four 120v loads (without actually naming the equipment), as follows: a 7 amp, a 6 amp, a 5 amp, and a 4 amp. I think the Example would have us pair the 12 and the 10, and show only a 12 amp contribution to the neutral, and then pair the 8 and the 7, thus showing another 8 amp contribution to the neutral, next then pair the 6 and the 5, thus showing another 6 amp contribution to the neutral, and finally list the 4 amp load separately, thus showing another 4 amp contribution to the neutral. The neutral contribution resulting from these 7 loads would be 12 + 0 + 8 + 0 + 6 + 0 + 4 = 30 amps.
[ June 16, 2003, 05:29 PM: Message edited by: charlie b ]