The question concerns the installation of five 3/c 500KCMIL with #2 EGC, paralleled feeder cables on a 2500KVA, 480V/277V transformer secondary switchgear feeder breaker.
The transformer is equipped with high resistance grounding that limits ground fault current to 5A. The system is set up to alarm when a ground fault occurs but does not trip.
The ampacity of the 5x500KCMIL feeder (not taking derating into account) is 1900A (5X380A=1900A). The ampacity of a single #2 EGC is 115A. The breaker OCPD is currently set to trip at 1600A phase overcurrent and 500A ground fault current (OCPD minimum ground fault setting).
The system is in an industrial facility with full time qualified electrical maintenance personnel.
Owing to the High Resistance Grounding System protecting the 1/c #2 EGC from current greater than 5A, does this arrangement have any effect on 2005 NEC 250.122(F) sub paragraph (2)(2) requirement for the provision of a ground fault protective device set to trip the breaker if ground fault current exceeds the EGC ampacity?
Does providing a high resistance grounding system that limits ground fault current to 5A (well below the 1-1/c #2 EGC ampacity of 11 ) and short circuit protection for the EGC conductor meet the intent of the code
The transformer is equipped with high resistance grounding that limits ground fault current to 5A. The system is set up to alarm when a ground fault occurs but does not trip.
The ampacity of the 5x500KCMIL feeder (not taking derating into account) is 1900A (5X380A=1900A). The ampacity of a single #2 EGC is 115A. The breaker OCPD is currently set to trip at 1600A phase overcurrent and 500A ground fault current (OCPD minimum ground fault setting).
The system is in an industrial facility with full time qualified electrical maintenance personnel.
Owing to the High Resistance Grounding System protecting the 1/c #2 EGC from current greater than 5A, does this arrangement have any effect on 2005 NEC 250.122(F) sub paragraph (2)(2) requirement for the provision of a ground fault protective device set to trip the breaker if ground fault current exceeds the EGC ampacity?
Does providing a high resistance grounding system that limits ground fault current to 5A (well below the 1-1/c #2 EGC ampacity of 11 ) and short circuit protection for the EGC conductor meet the intent of the code