After reading the above NEC section I noticed a contradiction. The first sentence begins:
Listed manual motor controllers additionally marked "Suitable as Motor Disconnect" shall be permitted as a disconnecting means where installed between the final motor branch-circuit short-circuit protective device and the motor.
The second sentence then reads:
Listed manual motor controllers additionally marked "Suitable as Motor Disconnect" shall be permitted as disconnecting means on the line side of the fuses permitted in 430.52(C)(5).
But the next sentence reads:
In this case, the fuses permitted in 430.52(C)(5) shall be considered supplementary fuses, and suitable branch-circuit short circuit and ground-fault protective devices shall be installed on the line side of the manual motor controller additionally marked "Suitable as Motor Disconnect".
Now the fuses in 430.52(C) were meant for branch circuits. Now why we do have a branch-circuit protective device connected on each side of the controller? The first sentence says that the controller is connected from the FINAL motor branch-circuit short-circuit protective device. Now how could this be if the controller is connected between two protective devices? I think there is something wrong with the second sentence because it states that protective devices are to be connected downstream from the controller.
Listed manual motor controllers additionally marked "Suitable as Motor Disconnect" shall be permitted as a disconnecting means where installed between the final motor branch-circuit short-circuit protective device and the motor.
The second sentence then reads:
Listed manual motor controllers additionally marked "Suitable as Motor Disconnect" shall be permitted as disconnecting means on the line side of the fuses permitted in 430.52(C)(5).
But the next sentence reads:
In this case, the fuses permitted in 430.52(C)(5) shall be considered supplementary fuses, and suitable branch-circuit short circuit and ground-fault protective devices shall be installed on the line side of the manual motor controller additionally marked "Suitable as Motor Disconnect".
Now the fuses in 430.52(C) were meant for branch circuits. Now why we do have a branch-circuit protective device connected on each side of the controller? The first sentence says that the controller is connected from the FINAL motor branch-circuit short-circuit protective device. Now how could this be if the controller is connected between two protective devices? I think there is something wrong with the second sentence because it states that protective devices are to be connected downstream from the controller.