tincan44
Member
- Location
- Indian River County, Fl.
Second paragraph:
"Where more than two NM cables containing two or more current-carrying conductors are bundled together and passing through wood framing that is to be fire- or draft-stopped using thermal insulation or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a)"
The commentary from the Handbook says:
"Section 310.15(B)(2)(a) states in part "or where single conductors or multiconductor cables are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing and are not installed in raceways, the allowable ampacity shall be reduced as shown in Table 310.15(B)(2)(a)." Failure to comply with the appropriate adjustment ampacity derating called for by this table, where nonmetallic cables may be stacked or bundled, can lead to overheating of conductors. For the 2005 Code a new requirement was added to prevent overheating of Type NM conductors where passing through draft- and fire-stopped material."
Sounds to me like electricians will be drilling more holes and maintaining spacing or be very surprised when they have to apply derating factors to their circuits.
"Where more than two NM cables containing two or more current-carrying conductors are bundled together and passing through wood framing that is to be fire- or draft-stopped using thermal insulation or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a)"
The commentary from the Handbook says:
"Section 310.15(B)(2)(a) states in part "or where single conductors or multiconductor cables are stacked or bundled longer than 600 mm (24 in.) without maintaining spacing and are not installed in raceways, the allowable ampacity shall be reduced as shown in Table 310.15(B)(2)(a)." Failure to comply with the appropriate adjustment ampacity derating called for by this table, where nonmetallic cables may be stacked or bundled, can lead to overheating of conductors. For the 2005 Code a new requirement was added to prevent overheating of Type NM conductors where passing through draft- and fire-stopped material."
Sounds to me like electricians will be drilling more holes and maintaining spacing or be very surprised when they have to apply derating factors to their circuits.