Davidh
Member
- Location
- Ukiah, California
Section 310.15(A)(1) states that ampacities for conductors shall be permited to be determined by tables as provided in 310.15(B).
Section 310.15(B) states that apmacities for conductors rated 0 to 2000 volts shall be as specified in the allowable ampacity table 310.16 thru 310.19, and ampacity table 310.20 and table 310.21 as modified by (B)(1) thru (b)(6).
Table 310.21 states Ampacities of Bare or Covered Conductors in Free Air Based on 104 F Ambient, 176F Total Conductor Temperature, 2ft/sec Wind Velocity.
The question is: Can triplex (covered conductor) be used for overhead conductors from a service to a subpanel at an outbuilding for a residence?
According to the code sections listed above it looks to me like the code allows this use without engineered supervision. One of the issues that was brought to my attention is how do you figure the ambient air and total conductor temperature and how do you figure the wind velocity without an engineer. Any help would be appreciated.
Section 310.15(B) states that apmacities for conductors rated 0 to 2000 volts shall be as specified in the allowable ampacity table 310.16 thru 310.19, and ampacity table 310.20 and table 310.21 as modified by (B)(1) thru (b)(6).
Table 310.21 states Ampacities of Bare or Covered Conductors in Free Air Based on 104 F Ambient, 176F Total Conductor Temperature, 2ft/sec Wind Velocity.
The question is: Can triplex (covered conductor) be used for overhead conductors from a service to a subpanel at an outbuilding for a residence?
According to the code sections listed above it looks to me like the code allows this use without engineered supervision. One of the issues that was brought to my attention is how do you figure the ambient air and total conductor temperature and how do you figure the wind velocity without an engineer. Any help would be appreciated.