From the 2005:
Inspectors/plans examiners: How will you ensure this is complied with?
The only thing I can think of is to do a fault current study on the design then study inverse time circuit breaker curves to make sure the branch circuit OCPD opens before the feeder or service OCPD opens. Or, I geuss you might be able to use current limitting breakers on the branch circuits??? What do you think?
700.27 Coordination. Emergancy system(s)overcurrent devices shall be selectively coordinated with all supply side overcurrent protective devices.
Definition from Art. 100701.18 Coordination. Legally required standby system(s)overcurrent devices shall be selectively coordinated with all supply side overcurrent protective devices.
Engineers/designers: How will you address this?Coordination (selective). Localization of an overcurrent condition to restrict outages to the circuit or equipment effected, accomplished by the choice of overcurrent protective devices and their ratings or settings/
Inspectors/plans examiners: How will you ensure this is complied with?
The only thing I can think of is to do a fault current study on the design then study inverse time circuit breaker curves to make sure the branch circuit OCPD opens before the feeder or service OCPD opens. Or, I geuss you might be able to use current limitting breakers on the branch circuits??? What do you think?