422.13 is driving me crazy.
It now says that water heaters are a continuous load. In the 2002, you had to provide 125% for the branch circuit conductors, but nowhere else.
So the question is, how does this relate to article 220? If I have dwelling unit with 4 appliances, I can apply a 75% demand factor to them...well, this makes no sense for something that is a continuous load! I've looked deeper into it, and I have noticed that 422.13 is not included in table 220.3. This is what I am comin up with:
1) The branch circuit must be sized at 125%, because of 210.19.
2) The feeder circuit must also be 125%, because of 215.2.
3) The service conductors must also be 125%, because of 230.42.
4) This new change in 422 does'nt not change anything in article 220, because it is not in table 220.3.
What do you guys think?
BTW: Sorry its been so long since I've posted
[ February 11, 2005, 12:33 PM: Message edited by: ryan_618 ]
It now says that water heaters are a continuous load. In the 2002, you had to provide 125% for the branch circuit conductors, but nowhere else.
So the question is, how does this relate to article 220? If I have dwelling unit with 4 appliances, I can apply a 75% demand factor to them...well, this makes no sense for something that is a continuous load! I've looked deeper into it, and I have noticed that 422.13 is not included in table 220.3. This is what I am comin up with:
1) The branch circuit must be sized at 125%, because of 210.19.
2) The feeder circuit must also be 125%, because of 215.2.
3) The service conductors must also be 125%, because of 230.42.
4) This new change in 422 does'nt not change anything in article 220, because it is not in table 220.3.
What do you guys think?
BTW: Sorry its been so long since I've posted
[ February 11, 2005, 12:33 PM: Message edited by: ryan_618 ]