Conductive reinforcing steel for coping and around pool in 4?concreate slab was installed by the flat workers. We have bonded the steel in 5 places around pool within 3? of pool wall. The inspector has the flat worker re-doing the steel as they were not 12 x 12 grid network. He quoted NEC 2005 680.26 (c) 3. It is my opinion that ?grid structure? in 680.26 c refers to the construction of a #8 awg bare solid copper grid network under (3) Alternate Means and the NEC does not give a specified construction method for 680.26 (c)1 or Structural Reinforcing Steel.
The General that we are working for called me two weeks prior to the installation of the re-bar and asked if the NEC had specifications regarding the installation of the re-bar. After reviewing the section I call back and my answer to his question was no. Do I deserve the egg that is on my face? Thanks for any and all comments. T. J.
The General that we are working for called me two weeks prior to the installation of the re-bar and asked if the NEC had specifications regarding the installation of the re-bar. After reviewing the section I call back and my answer to his question was no. Do I deserve the egg that is on my face? Thanks for any and all comments. T. J.