Remote buiding / office trailers
Remote buiding / office trailers
1) Correct and EGC sized to Table 250.122.
2) What bonding jumper?
3) Correct.
4) Correct (and I make note that you did not reference the section-corresponding table).
I have the following conditions which I believe that my description below is the only code compliant installation. I have a fellow worker that believes I am incorrect with my interpretation of the NEC 2008 for this installation.
1 - I have six separate metal office trailers on the same property.
2 - The six office trailers are powered from the same outdoor remote sub panel.
3 - The six office trailers are about four feet apart from each other.
4 - Each office trailer has it own feeder installed from the outdoor remote sub panel to the interior panel of each trailer.
5 - There is no metallic piping of any kind between the six metal office trailers.
6 - Each office trailer has a three phase interior panel with separate neutral and equipment grounding conductor bar and conductors.
I believe that the following applies to this installation.
A - NEC 250.32 ( B ) applies and describes the proper installation for the above listed conditions
B - Each trailer must be bonded from its interior panel that supplies it's power. 250.32 ( B )
C - Each trailer must be connected to a grounding electrode system. 250.64
D - The bonding jumper to the building steel must be sized to 250.66, according to 250.104 ( C )
E - The six trailers can be connected to a common grounding electrode system. 250.58, 250.64 ( D ) ( 1 )
F - The six trailers CAN NOT be BONDED from the remote sub panel that supplies power to all six units.
Feedback please.