7-74 Log #3152 NEC-P07
Final Action: Accept
(334.80)
____________________________________________________________
Submitter:
Travis Lindsey, Travis Lindsey Consulting Services
Recommendation:
Add an additional third paragraph to 334.80 to read:
Where more than two NM cables containing two or more current-carrying
conductors are installed in contact with thermal insulation without maintaining
spacing between cables, the allowable ampacity of each conductor shall be
adjusted in accordance with Table 310.15(B)(2)(a).
Substantiation:
Recent field experimentation shows that NM cables which are
grouped or bundled together for varying lengths and installed in contact with
thermal insulation in walls and ceilings can exceed the maximum allowable
design temperatures of the insulation. Even when the circuit currents were
limited to eight percent or less, temperature exceeded 90?C (194?F).
Full details are contained in the test report entitled
NM Cable Bundles
Installed on or In Thermal Insulation, November 2005.
Note: Supporting material is available for review at NFPA Headquarters.
Panel Meeting Action: Accept
Number Eligible to Vote: 14
Ballot Results:
Affirmative: 13 Negative: 1
Explanation of Negative:
ADAMS, M.: NECA believes this proposal is too restrictive. ?In contact with
thermal insulation? is not the same concept as in the present second paragraph,
which envisions completely surrounding bundled NM cables with thermal
insulation or sealing foam. Also, since ?bundled? is not a term defined in the
NEC, accepting this proposal could preclude use of standoff type cable clamps.
While intended to maintain space between adjacent NM cables, multiple cables
installed in standoff clamps still touch in places, and might also touch thermal
insulation. We do not believe that NM cables should be derated under this
installation circumstance.