willdalrymple
Member
- Location
- Texas
do I understand the 2008 table and its corrisponding information correctly, that if I were going to run a new line to a Sub-panel in the attic for the furnace air handler that requires a minimum ampacity of 104.5 amps I would have to use table 310-16 and use # 2 copper. and not the #3 copper listed in the table 310-15