2008 code change

Status
Not open for further replies.

gei3137

Member
I have found out from our inspector the 2008 code does not allow nm cable to be installed in pvc conduit or carflex outside above grade. They consider this to be a wet location. Since mn cable is only allowed in dry locations this is now a violation. Has anybody else heard about this
 

iwire

Moderator
Staff member
Location
Massachusetts
Actually that as been a violation for a long time, in the 2008 NEC they just made it more clear.

The inside of a raceway is considered a wet location when the raceway itself is in a wet location.
 