2008 code

Status
Not open for further replies.

tdjs

Member
Whats the 2008 code on sizing Alum. SER cable from a 400 amp 120/240 volt single phase service with main to two 200 amp panels in a house? What temp. factor do I use for sizing 60 or 75 degree?
 
Don't take this wrong, but if you're doing installations under the 2008 NEC you need to invest in a 2008 code book, the answers you get here may or may not be correct and you would need to check them yourself.

Roger
 
Whats the 2008 code on sizing Alum. SER cable from a 400 amp 120/240 volt single phase service with main to two 200 amp panels in a house? What temp. factor do I use for sizing 60 or 75 degree?

60C for feeders.

338.10 said:
(4) Installation Methods for Branch Circuits and Feeders.
(a) Interior Installations. In addition to the provisions of this article, Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Part II of Article 334.
FPN: See 310.10 for temperature limitation of conductors.
(b) Exterior Installations. In addition to the provisions of this article, service-entrance cable used for feeders or branch circuits, where installed as exterior wiring, shall be installed in accordance with Part I of Article 225. The cable shall be supported in accordance with 334.30. Type USE cable installed as underground feeder and branch circuit cable shall comply with Part II of Article 340.

Key words is that it must comply with nm cable (article 334)
 