Hello,
The last sentence of 2008 NEC 338.10(B)(4)(b) reads "Type USE cable installed as underground feeder and branch circuit cable shall comply with Part II of Article 340". Part II of Article 340 includes 340.80, which limits UF cable to 60C ampacity. Does this mean that if type USE cable is direct buried as a feeder, it is limited to 60C ampacity?
Thanks,
Wayne
The last sentence of 2008 NEC 338.10(B)(4)(b) reads "Type USE cable installed as underground feeder and branch circuit cable shall comply with Part II of Article 340". Part II of Article 340 includes 340.80, which limits UF cable to 60C ampacity. Does this mean that if type USE cable is direct buried as a feeder, it is limited to 60C ampacity?