Please read the substantiation provided for proposal #17-164 below. Unless I'm looking at it incorrectly it would seem that the submitter intends that the person using the tub be able to reset a tripped GFCI receptacle, protecting said tub motor, while still sitting in the actual tub? Am I looking at this wrong, or is that what was given as substantiation for the "readily accessible" requirement in the '08 code?
17-164 Log #2343 NEC-P17 Final Action: Accept in Principle
(680.71)
____________________________________________________________
Submitter: Andre R. Cartal, Princeton Borough Building Dept.
Recommendation: Add new text:
A GFCI receptacle shall not be located in the tub motor space or cavity.
Substantiation: The installation of a GFCI type receptacle in the tub motor
space is not apparent to the average homeowner as evidenced by the many
complaints received in our office. Even if the tub occupant is aware of the
location of the receptacle, it does not seem appropriate to expect a person to
exit the tub and remove the side of the tub or the access panel to reset the
receptacle.
Panel Meeting Action: Accept in Principle
Panel Statement: See panel action on Proposal 17-165.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
____________________________________________________________
17-165 Log #2547 NEC-P17 Final Action: Accept in Principle
(680.71)
____________________________________________________________
Submitter: Robert P. McGann, City of Cambridge
Recommendation: Revise text to read as follows:
Hydromassage bathtubs and their associated electrical components must be
on dedicated circuit(s) and shall be (protected by a) ground-fault interrupter.
Substantiation: If it is not spelled out in the listing papers, contractors are
tapping in on hallway, living room and/or bedroom circuit without a violation.
Panel Meeting Action: Accept in Principle
Change 680.71 to read as follows:
Hydromassage bathtubs and their associated electrical components shall be
on a dedicated circuit and protected by a readily accessible ground-fault
circuit interrupter. All 125-volt, single-phase receptacles not exceeding 30
amperes and located within 1.5 m (5 ft) measured horizontally of the inside
walls of a hydromassage tub shall be protected by a ground-fault circuit
interrupter(s).
Panel Statement: The change meets the submitter?s intent.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
Pete
17-164 Log #2343 NEC-P17 Final Action: Accept in Principle
(680.71)
____________________________________________________________
Submitter: Andre R. Cartal, Princeton Borough Building Dept.
Recommendation: Add new text:
A GFCI receptacle shall not be located in the tub motor space or cavity.
Substantiation: The installation of a GFCI type receptacle in the tub motor
space is not apparent to the average homeowner as evidenced by the many
complaints received in our office. Even if the tub occupant is aware of the
location of the receptacle, it does not seem appropriate to expect a person to
exit the tub and remove the side of the tub or the access panel to reset the
receptacle.
Panel Meeting Action: Accept in Principle
Panel Statement: See panel action on Proposal 17-165.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
____________________________________________________________
17-165 Log #2547 NEC-P17 Final Action: Accept in Principle
(680.71)
____________________________________________________________
Submitter: Robert P. McGann, City of Cambridge
Recommendation: Revise text to read as follows:
Hydromassage bathtubs and their associated electrical components must be
on dedicated circuit(s) and shall be (protected by a) ground-fault interrupter.
Substantiation: If it is not spelled out in the listing papers, contractors are
tapping in on hallway, living room and/or bedroom circuit without a violation.
Panel Meeting Action: Accept in Principle
Change 680.71 to read as follows:
Hydromassage bathtubs and their associated electrical components shall be
on a dedicated circuit and protected by a readily accessible ground-fault
circuit interrupter. All 125-volt, single-phase receptacles not exceeding 30
amperes and located within 1.5 m (5 ft) measured horizontally of the inside
walls of a hydromassage tub shall be protected by a ground-fault circuit
interrupter(s).
Panel Statement: The change meets the submitter?s intent.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
Pete