2008 nec article 250.146 B

Status
Not open for further replies.

grumpy11

Senior Member
ok lets look at this. simple outlet in wall. 2 wire ac cable to box adapter ring on box. sheet rock wall,

useing self grounding device. does the device have to be bonded to box if there is no metal to metal contact from device to adapter.
 
ok lets look at this. simple outlet in wall. 2 wire ac cable to box adapter ring on box. sheet rock wall,

useing self grounding device. does the device have to be bonded to box if there is no metal to metal contact from device to adapter.

The self grounding receptacle is permitted to be used without an additional jumper when screwed to a grounded metal adapter cover.
 
yes but does it have to be metal to metal . last 2 words in article. flush-type box.

that wpould mean metal to metal to me.
 
yes but does it have to be metal to metal . last 2 words in article. flush-type box.

that would mean metal to metal to me.

The screw penetrates the yoke then spring on the back of the yoke and the screw inserts into the box and completes the bond.


The same thing would apply in 25o.146(A) when you remove the insulating washer off of a regular receptacle. When the screw is drawn up and contacts the box the bond is complete.
 
The screw penetrates the yoke then spring on the back of the yoke and the screw inserts into the box and completes the bond.


The same thing would apply in 25o.146(A) when you remove the insulating washer off of a regular receptacle. When the screw is drawn up and contacts the box the bond is complete.

Sorry I should have said completes the ground for the receptical not the bond.
 