Question has come up on a project in regards to any requirements for 'branch circuits' to be protected in the same manner which the article requires 'feeder-circuit wire' to be protected. The following is a deduction for not protecting the branch circuits in the same manner as the feeder-circuit and the feeder circuit equipment:
1. Article 700.9(D)(1),specifically states feeder-circuit wiring, with no mention of branch circuitwiring. Article 708.10 of the COPS article, which is not applicable to this project, specifically notes Feeder and Branch Circuit Wiring, specifically708.10(D) for branch circuits. This project's applicable section does not include the branch circuit wiring portion.
2. Article 100 definesboth 'Feeder' and 'Branch Circuit', with separate definitions, defining each individually, and not the same.
3. Article 700.9(D)(2)references feeder circuit equipment, for feeder circuits, which includes, transfer switches, transfromers, and panels, thus further defining feeder circuit wiring as the wiring between these types of equipment. This section does not list branch circuit outlets/loads, nor the wiring between these loads and the panel, or per Article 100, branch circuits.
4. Emergency System Circuits for Lighting and Power are specifically referenced as Branch circuits including Articles 700.15, 700.16, 700.17, and 700.18, and these do not mention any branch circuit wiring requirements or to comply with Article 700.9.
Is it a requirement by the article to protect the branch circuits?
thanks for any of your thoughts on this....
1. Article 700.9(D)(1),specifically states feeder-circuit wiring, with no mention of branch circuitwiring. Article 708.10 of the COPS article, which is not applicable to this project, specifically notes Feeder and Branch Circuit Wiring, specifically708.10(D) for branch circuits. This project's applicable section does not include the branch circuit wiring portion.
2. Article 100 definesboth 'Feeder' and 'Branch Circuit', with separate definitions, defining each individually, and not the same.
3. Article 700.9(D)(2)references feeder circuit equipment, for feeder circuits, which includes, transfer switches, transfromers, and panels, thus further defining feeder circuit wiring as the wiring between these types of equipment. This section does not list branch circuit outlets/loads, nor the wiring between these loads and the panel, or per Article 100, branch circuits.
4. Emergency System Circuits for Lighting and Power are specifically referenced as Branch circuits including Articles 700.15, 700.16, 700.17, and 700.18, and these do not mention any branch circuit wiring requirements or to comply with Article 700.9.
Is it a requirement by the article to protect the branch circuits?
thanks for any of your thoughts on this....