2008 NEC GFCI requirements

Status
Not open for further replies.

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I had a list of the 2005 NEC added GFCI requirements, it was 14 or so.
Has anyone made a list of the 2008 NEC GFCI requirements, including the deletions of exceptions?
 
From the 08 NECHB

210.8(A)(2) & (A)(5): Expanded GFCI protection requirements by deleting exceptions for receptacles that are not readily accessible and receptacles located in dedicated spaces to supply an appliance.

? 210.8(B)(4): Expanded GFCI protection requirements to include all outdoor 15- and 20-ampere, 125-volt receptacles, and added a conditional exception to permit use of assured equipment grounding conductor program in industrial establishments.

? 210.8(B)(5): Added GFCI protection requirements for all 15- and 20-ampere 125-volt receptacles installed within 6 ft of the outside edge of sinks, and added exceptions for receptacles in industrial laboratories where the loss of power would introduce a greater hazard and for receptacles in patient care areas where critical care equipment may be utilized.
 
tom baker said:
I had a list of the 2005 NEC added GFCI requirements, it was 14 or so.
Has anyone made a list of the 2008 NEC GFCI requirements, including the deletions of exceptions?

Just residential or residential and commercial?

If commercial, don't forget repair areas in Chapter 5 and vending machines.
 