As shown in exhibit 700.5, I have multiple feeders into a building from a generator, and terminating on individually enclosed circuit breakers inside. Two of the feeders are parallel conductor sets each rated for 600A, and the other feeder is one set of conductors rated for 150A. The 600A feeders are (2) sets of 4#350+G, and the 150A feeder is 4#1/0+G. There is a total number of (5) conductors per phase for the three feeders.
If the generator breaker is 1200A, and has 4 lugs per phase rated for #3/0-500MCM, can I terminate the (5) sets of conductors at the generator breaker? If not, please let me know your thoughts on the conductor termination methods at the generator breaker.
Thanks
If the generator breaker is 1200A, and has 4 lugs per phase rated for #3/0-500MCM, can I terminate the (5) sets of conductors at the generator breaker? If not, please let me know your thoughts on the conductor termination methods at the generator breaker.
Thanks