What do you guys think?
342 IMC, 344 RMC, 352 RNC, 358 EMT .30 new part (C)
(C) Unsupported raceways: Type xxxxxx shall be permitted to be unsupported where the raceway is not more than 900 mm (3 ft) in length and remains in unbroken lengths (without coupling). Such raceway shall terminate in an outlet box, junction box, device box, cabinet, or other termination at each end of the raceway.
Substantiation: Unsupported raceways are violations of the code that occur everyday. As written, a 3? length of conduit between enclosures is required to be supported, despite the fact that it adds little if any structural value to the system. Quite often, particularly with conduit nipples, securing and supporting a raceway shorter than 36? is not possible. Furthermore, securing and supporting is of little value on lengths less than 36? where the conduit terminates at a box on each end, where the box is installed and supported in compliance with its applicable code section.
This proposal is written with the parallel effect of code sections that have been strived for in chapter 3, and matches the numbering system used in the cable articles. It also uses existing text taken from both the cable articles and the raceway articles.
342 IMC, 344 RMC, 352 RNC, 358 EMT .30 new part (C)
(C) Unsupported raceways: Type xxxxxx shall be permitted to be unsupported where the raceway is not more than 900 mm (3 ft) in length and remains in unbroken lengths (without coupling). Such raceway shall terminate in an outlet box, junction box, device box, cabinet, or other termination at each end of the raceway.
Substantiation: Unsupported raceways are violations of the code that occur everyday. As written, a 3? length of conduit between enclosures is required to be supported, despite the fact that it adds little if any structural value to the system. Quite often, particularly with conduit nipples, securing and supporting a raceway shorter than 36? is not possible. Furthermore, securing and supporting is of little value on lengths less than 36? where the conduit terminates at a box on each end, where the box is installed and supported in compliance with its applicable code section.
This proposal is written with the parallel effect of code sections that have been strived for in chapter 3, and matches the numbering system used in the cable articles. It also uses existing text taken from both the cable articles and the raceway articles.