2008's 250.32(B) - Detached Structure Feeders
George Stolz
Windsor, CO NEC: 2023
Hospital Master Electrician
We recently had a discussion about grandfather laws and whatnot, and looking at the new text for 250.32(B), I'm left a little confused.
It's generally accepted that previously compliant installations do not have to be upgraded to meet today's code. Under what conditions would you expect to be able to use 250.32(B)'s exception?
A new garage would not be permitted.
An old garage would not be required to be changed.
So when would you use this? :confused:
So there is an exception to allow ones that are installed to remain?
Bare with me, I do not buy a 2008 till I can get one with the MA amendments. :)
This is my guess.
I believe this section is written in to allow an existing situation. Suppose you had an existing 3 wire feeder to a detached garage. Now you are going to have to get inspection because you are adding circuits to the structure. In this case the exception comes into play to allow this situation. The inspector cannot make you change the feeder.
George, I'm sure you are aware that was submitted by Mike. I'm thinking Ryan may be of some help.
As I read it, it says:
Exception: For existing premises wiring systems only...
As long as the requirements of the execption are met, IMO call me Grandpa.
Sorry, here's the text:
I would say Dennis nailed it.
You could do a panel upgrade and there would be no question the 3 wire feeder could remain.....even though it is kind of grandfathered already. :confused: