200A 3phase al min wire size
This sounds like a study question so tell us what you think and how you arrived at your answer. We can help you after that.
Roger
Does it even matter if it is 3ph or single phase? It has to do with current being carried by the conductors, and not given that info.
OP said the panel is 200A. There's no requirement to provide that panel with a 200 amp feeder. So the minimum size is number 12, Post number 4.
Come on, you know that is not what the question is asking even though it cannot be truly answered without a load calc. I suspect they are looking for 250kcm as the minimum size for 200 amps. Bad question
Although the question lacks a few details I agree that it's very likely that he's asking for the conductor size for a 200 amp feeder. 250 kcmil AL would give the full 200 amps, #4/0 will give you 180 amps next size up rule 200 amps.