in a commercial building 200a 3phase sub panel at 125ft away what is the minim size aluminum feeder wire size I can use
In addition, I would say there is not enough information to answer the question. We could make some logical assumptions and give answers based on that of course.This sounds like a study question so tell us what you think and how you arrived at your answer. We can help you after that.
Roger
The minimum size for AL conductors is #12. See 310.5. however I am not sure anyone makes it, the smallest you might be able to practically get is #6.in a commercial building 200a 3phase sub panel at 125ft away what is the minim size aluminum feeder wire size I can use
You would need to provide the calculated load but for the 200 amps the minimum size required would be #4/0.in a commercial building 200a 3phase sub panel at 125ft away what is the minim size aluminum feeder wire size I can use
OP said the panel is 200A. There's no requirement to provide that panel with a 200 amp feeder. So the minimum size is number 12, Post number 4.Oops missed the reference yo 200A
Come on, you know that is not what the question is asking even though it cannot be truly answered without a load calc. I suspect they are looking for 250kcm as the minimum size for 200 amps. Bad questionOP said the panel is 200A. There's no requirement to provide that panel with a 200 amp feeder. So the minimum size is number 12, Post number 4.
Although the question lacks a few details I agree that it's very likely that he's asking for the conductor size for a 200 amp feeder. 250 kcmil AL would give the full 200 amps, #4/0 will give you 180 amps next size up rule 200 amps.Come on, you know that is not what the question is asking even though it cannot be truly answered without a load calc. I suspect they are looking for 250kcm as the minimum size for 200 amps. Bad question
We're probably not getting the exact wording of the question.Bad question
I know I know, I'm just having some fun. This is MH, can't give too simple of a responseCome on, you know that is not what the question is asking even though it cannot be truly answered without a load calc. I suspect they are looking for 250kcm as the minimum size for 200 amps. Bad question
I know I know, I'm just having some fun. This is MH, can't give too simple of a response![]()
People can go over to ET for the simple one line responses
But, it might not be the "right" answer.. Here, you get 12 answers and you can pick the one you likePeople can go over to ET for the simple one line responses![]()
Indeed. My answer or #12 AL would be very cost competitive.But, it might not be the "right" answer.. Here, you get 12 answers and you can pick the one you like![]()
if you could get it.Indeed. My answer or #12 AL would be very cost competitive.
I think you can get #8 too.The minimum size for AL conductors is #12. See 310.5. however I am not sure anyone makes it, the smallest you might be able to practically get is #6.