I've got a question and want to get the opinion of the learned members of this forum.
I'm getting ready to tun a 200A feed from a outside main to a inside MLO panel. I can get a good deal on some 4/0 aluminun quad plex but I have a few questions.
The cable has two 4/0, one 2/0 and one #4 for the equipment grounding conductor. The conductors are rated USE/RHH/RHW. The feeder will be 28 feet long. Ordinarily I would use a bigger grounding conductor although 250.122 allows #4 aluminum for 200 amps.
Would you use it? If not, why not.
I normally use copper inside a home, but you know how it is with prices these days.
steve