Running SE indoors, not through insulation, currently on 2011 code. Can you put 4/0-4/0-4/0-2/0 SE cable on a 200A breaker if the panel manufacturer doesn't make a 180A breaker?
That only applies if there isn't a standard breaker size?Yes as long as the calculated load is 180 amps or less.
The calculated load is 180 or less then you can use the 200 amp breaker. There is no 180 amp breaker( art. 240.6(A)) as a standard size so 240.4(B) allows use to go up if the load is not more than the ampacity of the conductor.That only applies if there isn't a standard breaker size?