200a ATS for single 200a panel

Status
Not open for further replies.

mcgee89

Member
Location
Spokane Wa
Occupation
Electrician
I have a 400a service with 2x 200a panels each being the service disconnect. They are both installed on the exterior on the house. Am I required to install a single 400a service disconnect when I install a 200 a ATS for one of the panels?


Sent from my iPhone using Tapatalk
 

Buck Parrish

Senior Member
Location
NC & IN
No - but of course you know the ATS has to isolate the generator powered portion of the service. It's a pretty common set up.

But wait , are you asking because of the emergency disco requirement? What code cycle?
 

mcgee89

Member
Location
Spokane Wa
Occupation
Electrician
Correct, that’s where the 200a service feed for that panel will come directly to the ATS then feed thru to the panel. In which I also will need to float the neutrals on that one panel.


Sent from my iPhone using Tapatalk
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I assume this is an all new installation, so why not two 200 amp disconnects to satisfy the emergency disconnect rule, then transfer switch and MLO panels? The AHJ may require an E-Stop for the generator grouped with the disconnects.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Ok, just re-read your post, so you already have two panels with service disconnects outside? If both are at the same location, the 400 would not be needed, unless the service disconnect in the service rated transfer switch is not easily accessible?
 

mcgee89

Member
Location
Spokane Wa
Occupation
Electrician
5f11668ec669cae366dbadd1d138d54c.jpg



Sent from my iPhone using Tapatalk
 

mcgee89

Member
Location
Spokane Wa
Occupation
Electrician
Both outside in this doghouse like accessible covering. Customer wants the ATS below the panel in this covered space.


Sent from my iPhone using Tapatalk
 