chainsaw_link
Member
- Location
- WA
- Occupation
- Journeyman
I'm in the process of installing a 200A ATS on a residential 200A panel. The ATS is SE rated and also emergency disconnect rated. The service to the house is 400A into the meter, which then feeds back to back into two 200A main breaker panels (two 200A service disconnects next to each other inside a garage that feed the 4000 Square ft house). I'm running into confusion over 230.85 emergency disconnects. If I put it outside, would it be considered an emergency disconnect and would I then be required to provide a second emergency disconnect for the panel I'm not working with in order to have them grouped? Or if I put it inside, directly next to the panel it will be supplying, does that constitute 'relocating' one of my service disconnects (even if it is now just the ATS), which would then require me to install an outdoor emergency disconnect? I am in Washington and here is their statement on when an emergency disconnect is required:
2020 NEC 230.85 requirements for emergency disconnects for one- and two-family dwellings will apply to all new dwellings having building permits issued on or after October 29, 2020. For service alterations made under electrical permits issued on or after October 29, 2020, a readily accessible outdoor emergency disconnecting means must be installed where services are increased or decreased in size, or where service disconnects, meter bases, overhead service masts, or underground service risers are relocated.
Seems like a catch 22. Is there anyway to not have to install an outdoor disconnect on the second 200A panel Im not even working with? Thanks.
2020 NEC 230.85 requirements for emergency disconnects for one- and two-family dwellings will apply to all new dwellings having building permits issued on or after October 29, 2020. For service alterations made under electrical permits issued on or after October 29, 2020, a readily accessible outdoor emergency disconnecting means must be installed where services are increased or decreased in size, or where service disconnects, meter bases, overhead service masts, or underground service risers are relocated.
Seems like a catch 22. Is there anyway to not have to install an outdoor disconnect on the second 200A panel Im not even working with? Thanks.